SAI – Safety analog input
Block SymbolLicensing group: ADVANCED
Function Description
The SAI block tests the input signal u and assesses its validity. The input signal u is considered invalid
(the output )
in the following cases:
- F1: Hardware error. The input signal .
- F2: The input signal u varies too little. The last nc samples of the input u lies within the
interval of width du,
where vmin and vmax are the lower and upper limits of the input u, respectively, and nbits is the number of A/D converter bits. The situation when the input signal u varies too little is shown in the following picture:
If the parameter nc is set to , the condition F2 is never fulfilled.
- F3: The input signal u varies too much. The last nr samples of the input u filtered by the
SPIKE filter have a span which is greater than rate,
where prate defines the allowed percentage change in the input signal u within the last nr samples (with respect to the overall range of the input signal ). The block includes a SPIKE filter with fixed parameters and suppressing peaks in the input signal to avoid undesirable fulfilling of this condition. See the SPIKE block description for more details. The situation when the input signal u varies too much is shown in the following picture:
If the parameter nr is set to , the condition F3 is never fulfilled.
- F4: The input signal u is out of range. The last nv samples of the input signal u lie out of the allowed
range .
If the parameter nv is set to , the condition F4 is never fulfilled.
The signal u is copied to the output y without any modification when it is considered valid. In the other case, the output y is determined by a substitute value from the sv input. In such a case the output E is set to on and the output iE provides the error code. The input R resets the inner error flags F1–F4. For the input R set permanently to on, the invalidity indicator E is set to on for only one cycle period whenever some invalidity condition is fulfilled. On the other hand, for , the output E is set to on and remains true until the reset (rising edge R: offon).
The table of error codes iE resulting from the inner error flags F1–F4:
| F1 | F2 | F3 | F4 | iE |
| 0 | 0 | 0 | 0 | 0 |
| 0 | 0 | 0 | 1 | 1 |
| 0 | 0 | 1 | 0 | 2 |
| 0 | 0 | 1 | 1 | 3 |
| 0 | 1 | 0 | 0 | 4 |
| 0 | 1 | 0 | 1 | 5 |
| 0 | 1 | 1 | 0 | 6 |
| 0 | 1 | 1 | 1 | 7 |
| 1 | * | * | * | 8 |
The nb parameter defines the number of samples which are not included in the validity assessment after initialization of the block (restart). Recommended setting is to allow the SPIKE filter initial conditions to fade away.
Inputs
u | Analog input of the block | Double (F64) |
sv | Substitute value to be used when the signal u is marked as invalid | Double (F64) |
HWF | Hardware error indicator | Bool |
|
|
|
R | Reset inner error flags F1–F4 | Bool |
Outputs
y | Analog output of the block | Double (F64) |
yf | Filtered analog output signal y, output of the SPIKE filter | Double (F64) |
E | Output signal invalidity indicator | Bool |
|
|
|
iE | Reason of invalidity | Long (I32) |
|
|
|
Parameters
nb | Number of samples which are not included in the validity assessment of the signal u after initialization of the block 10 | Long (I32) |
nc | Number of samples for invariability testing (the F2 condition) 10 | Long (I32) |
nbits | Number of A/D converter bits 12 | Long (I32) |
nr | Number of samples for variability testing (the F3 condition) 10 | Long (I32) |
prate | Maximum allowed percentage change of the input u within the last nr samples (with respect to the overall range of the input signal ) 10.0 | Double (F64) |
nv | Number of samples for out-of-range testing (the F4 condition) 1 | Long (I32) |
vmin | Lower limit for the input signal u -1.0 | Double (F64) |
vmax | Upper limit for the input signal u 1.0 | Double (F64) |