Getting started with REXYGEN on UniPi v1.1
1.4.5 REXYGEN Diagnostics
2.1 Windows 7/8/10
3 Installing the runtime modules of the REXYGEN system on Raspberry Pi
3.1 Installation of REXYGEN runtime
3.1.1 Installation with a script
3.1.2 Manual installation
3.2 Starting the runtime
3.3 Installed files and folders
3.4 Uninstall procedure
4 Configuration, compilation and execution
4.1 Creating a new project
4.2 Compiling and running a project
4.3 Adding a user interface (HMI)
4.4 Ready for interaction with the outer world
5 I/O configuration for the UniPi v1.1
5.1 Physical connections
5.2 Adding inputs and outputs to the project
5.3 Working with I/O signals
5.3.1 Modifications in the project main file
5.3.2 Modifications in the task
5.4 Updating the HMI
5.5 Additional information
5.5.1 Detailed description of the driver
5.5.2 Examples
6 Summary
The runtime core of the REXYGEN system turns your Raspberry Pi into a programmable device which will run your algorithms.
- Wide family of supported devices and input-output units (including UniPi v1.1)
REXYGEN Studio is a developer’s tool which runs on a standard PC with Windows. You create the algorithms using the function block library (The IEC 61131-3 standard defines Function Block Diagram (FBD) as one of the PLC programming techniques.) of the REXYGEN system [1]. The library contains simple comparators and timers as well as advanced blocks for signal processing and feedback control (PID controllers etc.). You compile your project on your PC and run it on your Raspberry Pi.
The REXYGEN HMI Designer is another developer’s tool intended for designing graphical user interface (or HMI, Human Machine Interface, if you prefer) for your algorithms. The user interface is included in the project and it is copied to your Raspberry Pi along with the algorithm.
The RexCore (REXYGEN runtime core) service runs on the target device (Raspberry Pi). Once installed, it runs in the background and therefore it is almost invisible for the user. It handles timing and execution of your algorithms and provides various services. The individual tasks are prioritized and executed using preemptive multitasking. The RexCore service is automatically started at system startup.
RexCore further contains an integrated webserver providing user interface (HMI) and REST API. Chapter 3 deals with installing all the necessary modules on Raspberry Pi.
With REXYGEN Diagnostics you can diagnose the runtime core and execution of your algorithm. It is an alternative standalone tool for commissioning and diagnostics of control algorithms. All the diagnostic functions are included in REXYGEN Studio, therefore REXYGEN Diagnostics can be considered obsolete. You can connect via local network or over the Internet.
This chapter describes the steps to install and uninstall the development tools of the REXYGEN system on Windows 7/8/10 operating systems. The tools also run on various GNU/Linux distributions using Wine (http://www.winehq.org).
2.1 Windows 7/8/10
The installation package of REXYGEN development tools contains the REXYGEN Studio and REXYGEN HMI Designer development environments, the REXYGEN Compiler compiler and the REXYGEN Diagnostics tool. It also includes the RexCore (REXYGEN runtime core) module for developing and testing purposes.
Follow the instructions for installation under Windows 7/8/10 given in section 2.1. The installation is started with wine REXYGEN-X.XX.XX.XXXX-PPP.exe command entered at the console prompt. Some distributions (e.g. Ubuntu) allow running the installator by clicking the REXYGEN-X.XX.XX.XXXX-PPP.exe file.
Pi
It is necessary to have a correctly configured Internet connection on your Raspberry Pi running the so-called Raspbian distribution of GNU/Linux (RexCore should also work on any other distribution based on Debian (e.g. Ubuntu).) prior to using this guide. Visit http://www.raspberrypi.org for more information.
REXYGEN runtime may be installed by adding a repository to the source list manually or with a script that automates all the installation tasks.
Currently, following platforms are supported for full automatic installation: plain Raspberry
Pi, Monarco HAT, UniPi 1.1, PiFace Digital.
For plain Raspberry Pi, run the following commands:
chmod +x rex-install-rpi.sh
sudo ./rex-install-rpi.sh
For Monarco HAT, run the following commands:
chmod +x rex-install-monarcohat.sh
sudo ./rex-install-monarcohat.sh
For UniPi version 1.1, run the following commands:
chmod +x rex-install-unipi1_1.sh
sudo ./rex-install-unipi1_1.sh
For PiFace Digital extension board, run the following commands:
chmod +x rex-install-pifacedigital.sh
sudo ./rex-install-pifacedigital.sh
These scripts always install the stable branch of REXYGEN. The scripts also provide --testing and --next parameters (e.g. sudo ./rex-install-rpi.sh --testing) to install development branches. The "testing" branch contains a REXYGEN version that is to be released soon, but still under testing. The "next" branch contains the current state of a next REXYGEN version under development. Use these options carefully.
Following instructions guide you through installation of REXYGEN runtime on plain Raspberry Pi. See documentation for other platforms for specific installation steps.
- Add REXYGEN public key:
wget -nc https://download.rexcontrols.com/files/key/rex-debian-key.pub
sudo apt-key add rex-debian-key.pub - Add the repository to /etc/apt/sources.list or create a *.list under /etc/apt/sources.list.d/
with the following content:
deb http://download.rexcontrols.com/repositories/debian-rex-2.50/ bullseye non-free
Replace bullseye with buster or stretch if you are still running the older Raspbian distribution. Replace debian-rex-2.50 with debian-rex-2.50-testing or debian-rex-2.50-next to install development branches. The "testing" branch contains a REXYGEN version that is to be released soon, but still under testing. The "next" branch contains the current state of a next REXYGEN version under development. Use these options carefully.
- Install REXYGEN runtime:
- Perform specific installation steps for your platform (Monarco HAT, UniPi 1.1, PiFace Digital etc.).
Right after the installation, the RexCore runtime module is started automatically in the background as a daemon and it is possible to establish connection between the host PC and the Raspberry Pi using the REXYGEN Studio program. RexCore also automatically runs upon system (re)start.
Use the following commands to remove REXYGEN runtime from the operating system:
sudo apt-get autoremove
The process of creating a control algorithm will be demonstrated on a very simple example with four Boolean variables representing manual switches. In Chapter 5.3, two of them will be replaced by physical inputs of the UniPi v1.1. A software timer will be used for measuring the time when the variables are true (i.e. the switches are in the ON position). A Boolean signal will indicate that the interval of predefined length has elapsed.
Enter the IP address of your Raspberry Pi in the Target field.
If there is no licence on your Raspberry Pi, you need to get one first. You can get a DEMO licence for free. See Appendix B for details and come back afterwards.
Note: There is also a standalone diagnostics program called REXYGEN Diagnostics. Click the REXYGEN Diagnostics
and confirm the IP address of the target platform.
All changes made while in the Watch mode are not permanently stored in the target device (unless you decide so, see [3]). Upon restarting the RexCore runtime module the algorithm will start with the parameters defined in the project source files, which were valid when compiling and downloading the algorithm to the target device. To apply the changes permanently, you have to transfer the changes to the source files and Compile and download the project one more time which defines new startup values.
moment. See [4] for details, it is a very interesting tool for developers and
- See [4] for detailed information about WebBuDi elements and possible customization (colors, backgrounds etc.).
- The default URL address is http://192.168.1.100:8008/hmi/index.html (replace 192.168.1.100 with the IP address of your UniPi v1.1).
We will use the input and output signals of the UniPi v1.1 for interaction with the real world.
As mentioned in Chapter 4, two physical switches will be connected as inputs and a software timer will control one output signal. In other words, this chapter is devoted to advancing from the generic example 0101-01 to example 0122-01 for the UniPi v1.1.
Connect the switches as shown below.
Now we tell the compiler to use the UniPi v1.1 I/O driver. To do this, edit the IODRV block parameters. Link the IODRV block with the RPiDrv module by setting
- – CASE SENSITIVE!
Continue editing the IODRV block parameters. For UniPi v1.1 set the following:
- – CASE SENSITIVE!
- Leave the cfgname parameter blank.
As the final step, rename the IODRV block to UNP, which will serve as a prefix for all I/O signals of this driver.
In the task double-click the input flag and set .Note the UNP prefix and two underscore characters. The first physical switch will be connected to digital input I01.
The second physical switch will be connected to I03 (UNP__IO3) and relay 1 will serve as the output signal (UNP__RLY1).
Similarly for other I/Os we could use the following flags:
- Goto, UNP__RLY8 – relay output 8
- From, UNP__I06 – digital input 6
- From, UNP__AI1 – analog input 1
A detailed description of the I/O driver for UniPi v1.1 is available in a separate manual [5].
After compiling the project and downloading it to the Raspberry Pi the control algorithm interacts with the physical world. Again it is possible to switch to Watch mode and observe the signals in real-time or analyze the trends of signals. Flip the physical switches and watch the signals.
A detailed description of the IO driver for UniPi v1.1 is available in a separate manual [5].
5.5.2 Examples
Start from an Example Project and select one of the UniPi v1.1 examples. As
Congratulations, you have created the example 0122-01 from scratch! You have learned how to develop, compile and run your algorithms on the Raspberry Pi. The interaction with sensors and actuators is provided via input-output driver of the REXYGEN system, which you have learned to configure and use.
Chapter 4 describes the creation of a simple WebBuDi user interface. The REXYGEN development tools also contain the REXYGEN HMI Designer program which is a tool for designing custom graphical visualizations from predefined components (Definition of custom components is also possible but it requires a bit of Javascript coding.). The REXYGEN HMI Designer is based on the well-known open-source vector editor InkscapeTM https://inkscape.org/en/.
You can find the description of each component and property in [4]. Leave the default values
The Browser requires a target device with running algorithm. Make sure the algorithm is running, see Section 4.2. Also the target URL must be set. Press Browse button. The login dialog will be opened. Change Target to 192.168.1.100:8008 (replace 192.168.1.100 with the IP address of your UniPi v1.1). Unless you changed the login credentials, use the default username admin with an empty password. After a successful login the connection tab is expanded with a tree-view of the running algorithm (you have already seen this tree-view in algorithm diagnostics).
As mentioned earlier, the *.hmi.svg files in the hmisrc folder are automatically processed while the project is compiled in the REXYGEN Studio application. The project main file must contain the HMI block with GenerateRexHMI parameter enabled. This was already covered in Section 4.3 so you should have everything ready.
Once you compile the project again and download it to your Raspberry Pi, the HMI will be
accessible via a web browser. Navigate to
of your UniPi v1.1). You will see your HMI with live data.
This tutorial covers only the very basic components. If you want to get more information about additional components, see [4].
- The RexCore runtime module always needs a licence to run on your Raspberry Pi. There are DEMO licences available at no cost and there are permanent licences which you can purchase. Each Raspberry Pi needs an individual licence.
Once successfully applied, your algorithm will download to your UniPi v1.1.
Evaluation version of RexCore (REXYGEN runtime core) is functional for 2 hours. It is possible to run your algorithm on the UniPi v1.1 but you cannot store it permanently. The algorithm resides only in the RAM memory therefore it will not run after a restart or power-up. You can use almost all function blocks, see [1]. The RexCore runtime core on the target device is terminated after 2 hours of operation in demo mode without any warning. After a restart, you have another 2 hours for your experiments.
[3] REX Controls s.r.o.. REXYGEN Studio – User manual, 2020. .
[4] REX Controls s.r.o.. REXYGEN HMI – User manual, 2020. .
[5] REX Controls s.r.o.. RPiDrv driver of REXYGEN for Raspberry Pi – user guide, 2020. .
Documentation reference number: 13771
2022 © REX Controls s.r.o., www.rexygen.com