Getting started with REXYGEN on UniPi Axon/Patron
1.4.5 REXYGEN Diagnostics
2.1 Windows 7/8/10
3 Installing the runtime modules of the REXYGEN system on UniPi Axon/Patron
3.1 Install using operating system image with REXYGEN
3.2 Manual installation on running UniPi Axon/Patron
3.3 Starting the runtime
3.4 Installed files and folders
4 Licensing REXYGEN using REXYGEN DWM on UniPi Axon/Patron
4.1 Obtaining a DEMO licence
4.2 Obtaining a permanent licence
4.2.1 Activation of the permanent licence
5 Default REXYGEN project on UniPi Axon/Patron
5.1 Control UniPi Axon/Patron from HMI
5.2 Control UniPi Axon/Patron through OPC UA
5.3 Loading project from UniPi Axon/Patron to REXYGEN Studio
6 Configuration, compilation and execution
6.1 Creating a new project
6.2 Compiling and running a project
6.3 Adding a user interface (HMI)
6.4 Ready for interaction with the outer world
7 I/O configuration for the UniPi Axon/Patron
7.1 Physical connections
7.2 Adding inputs and outputs to the project
7.3 Working with I/O signals
7.3.1 Modifications in the project main file
7.3.2 Modifications in the task
7.4 Updating the HMI
7.5 Additional information
7.5.1 Detailed description of the driver
7.5.2 Examples
8 Summary
The runtime core of the REXYGEN system turns your UniPi Axon/Patron into a programmable device which will run your algorithms.
- Wide family of supported devices and input-output units (including UniPi Axon/Patron)
REXYGEN Studio is a developer’s tool which runs on a standard PC with Windows. You create the algorithms using the function block library (The IEC 61131-3 standard defines Function Block Diagram (FBD) as one of the PLC programming techniques.) of the REXYGEN system [1]. The library contains simple comparators and timers as well as advanced blocks for signal processing and feedback control (PID controllers etc.). You compile your project on your PC and run it on your UniPi Axon/Patron.
The REXYGEN HMI Designer is another developer’s tool intended for designing graphical user interface (or HMI, Human Machine Interface, if you prefer) for your algorithms. The user interface is included in the project and it is copied to your UniPi Axon/Patron along with the algorithm.
The RexCore (REXYGEN runtime core) service runs on the target device (UniPi Axon/Patron). Once installed, it runs in the background and therefore it is almost invisible for the user. It handles timing and execution of your algorithms and provides various services. The individual tasks are prioritized and executed using preemptive multitasking. The RexCore service is automatically started at system startup.
RexCore further contains an integrated webserver providing user interface (HMI) and REST API. Chapter 3 deals with installing all the necessary modules on UniPi Axon/Patron.
With REXYGEN Diagnostics you can diagnose the runtime core and execution of your algorithm. It is an alternative standalone tool for commissioning and diagnostics of control algorithms. All the diagnostic functions are included in REXYGEN Studio, therefore REXYGEN Diagnostics can be considered obsolete. You can connect via local network or over the Internet.
This chapter describes the steps to install and uninstall the development tools of the REXYGEN system on Windows 7/8/10 operating systems. The tools also run on various GNU/Linux distributions using Wine (http://www.winehq.org).
2.1 Windows 7/8/10
The installation package of REXYGEN development tools contains the REXYGEN Studio and REXYGEN HMI Designer development environments, the REXYGEN Compiler compiler and the REXYGEN Diagnostics tool. It also includes the RexCore (REXYGEN runtime core) module for developing and testing purposes.
Follow the instructions for installation under Windows 7/8/10 given in section 2.1. The installation is started with wine REXYGEN-X.XX.XX.XXXX-PPP.exe command entered at the console prompt. Some distributions (e.g. Ubuntu) allow running the installator by clicking the REXYGEN-X.XX.XX.XXXX-PPP.exe file.
Axon/Patron
Before installing the runtime modules of the REXYGEN system, it is possible to backup actual
state of your UniPi Axon/Patron. The process of Cloning, Backup & Restoration of OS images
can be found here:
https://kb.unipi.technology/en:hw:01-axon:backup2usb.
IMPORTANT: This procedure will delete all old data and settings. Make sure you have all the necessary files stored elsewhere!
- It is highly recommended to use the official UniPi Axon/Patron OS image with
REXYGEN which you can download from
http://rexygen.com/downloads/axon-rexygen_image.zip. - After you download the file, flash the Operating System according to this manual:
https://kb.unipi.technology/en:hw:01-axon:image.
It is also possible to install the RexCore (REXYGEN runtime core) on running UniPi Axon/Patron manually. Following instructions guide you through installation of REXYGEN runtime on plain UniPi Axon/Patron OpenSource OS. See documentation for other platforms for specific installation steps.
- Install some necessary packages:
sudo apt install wget gnupg2 - Add REXYGEN public key:
wget -nc https://download.rexcontrols.com/files/key/rex-debian-key.pub
sudo apt-key add rex-debian-key.pub - Add the repository to /etc/apt/sources.list or create a new *.list under
/etc/apt/sources.list.d/ with the following content:
deb http://download.rexcontrols.com/repositories/debian-rex-2.50/ bullseye non-free
deb http://download.rexcontrols.com/repositories/rex-dwm/debian bullseye non-freeReplace bullseye with buster or stretch if you are still running the older Debian distribution. Replace debian-rex-2.50 with debian-rex-2.50-testing or debian-rex-2.50-next to install development branches. The "testing" branch contains a REXYGEN version that is to be released soon, but still under testing. The "next" branch contains the current state of a next REXYGEN version under development. Use these options carefully.
sudo apt install rex-dwm
Right after the installation, the RexCore runtime module is started automatically in the background as a daemon and it is possible to establish connection between the host PC and the UniPi Axon/Patron using the REXYGEN Studio program. RexCore also automatically runs upon system (re)start.
The first thing you will need is to get the license. The fastest way is to use the REXYGEN DWM tool. Open your web-browser and input IP address of UniPi Axon/Patron. You should see the Device is not licensed! message on the bottom of the screen. Please, click on the Licensing.
- The RexCore runtime module always needs a licence to run on your UniPi Axon/Patron. There are DEMO licences available at no cost and there are permanent licences which you can purchase. Each UniPi Axon/Patron needs an individual licence.
Click on Get demo licence and you will be redirected to the registration form. Identify yourself and you’ll receive a DEMO licence key via e-mail. The licence key is called a SiteKey.
Once you have your DEMO licence key (SiteKey), apply it in REXYGEN DWMby selecting Apply Licence Keys and clicking on Apply keys.
Evaluation version of RexCore (REXYGEN runtime core) is functional for 2 hours. It is possible to run your algorithm on the UniPi Axon/Patron but you cannot store it permanently. The algorithm resides only in the RAM memory therefore it will not run after a restart or power-up. You can use almost all function blocks, see [1]. The RexCore runtime core on the target device is terminated after 2 hours of operation in demo mode without any warning. After a restart, you have another 2 hours for your experiments.
Each device running the RexCore runtime module is identified by the so-called SiteID tag. The purchased licence is associated with the hardware device, i.e. with the SiteID tag.
- Open your favorite web-browser on the desktop PC and fill in the IP address of
UniPi Axon/Patron. Once the DWM appears, select Licensing
Apply Voucher and enter your licence voucher code.
- If other licenses are already present, a new window will appear where you can
specify what should happen to the old licenses. Use the Overwrite option if the
UniPi Axon/Patron is running in DEMO mode. This is the last and irreversible
in your device, which is shown in the Active License panel. The licence key allows
permanent operation of the runtime core. It is highly recommended to check the licence
again after a reboot of the device.
In order to help you speed up a start with REXYGEN and UniPi Axon/Patron we have create an example project for most UniPi Axon/Patron which is already preinstalled on the image with REXYGEN (installation is described in Section 3.1). The project serves as a basic validation of the installation process and as a starting point for more complex applications. One can control digital output(s) DO, analog output(s) AO, observe the state of digital inputs(s) DI and analog input(s) AI. These general inputs and outputs are present on all UniPi Axon/Patron models. The steps to create and develop a new project from scratch is described in Chapter 6 in detail.
IMPORTANT: If you have valid permanent licence stored on your UniPi Axon/Patron,
this project will start automatically once RexCore (REXYGEN runtime core) starts. Otherwise,
if you have only a Demo license, you must compile and download the project from the
REXYGEN Studio on the UniPi Axon/Patron first. The project can be opened in the
REXYGEN Studio using either the procedure described in Section 5.3, or the project
can also be found in the Examples library as 0127-02_UniPi_Axon_Generic (All
examples which are part of the installation are marked by an ExampleID. The most
up-to-date examples are available with the latest installation of development tools or at
https://www.rexygen.com/example-projects/ ).
The process of compiling and running the project is described in Section 6.2.
The project contains graphical user interface (so-called Human-Machine-Interface) for easy control and observing of general outputs and inputs. The HMI can be found at URL address http://192.168.1.100:8008/hmi/index.html (replace 192.168.1.100 with the IP address of your UniPi Axon/Patron).
You can use the OPC UA interface to control your UniPi Axon/Patron too. Install any OPC
UA Client and connect to the OPC UA Server, which is running right now on your UniPi
Axon/Patron. There is the UAExport software used in this tutorial:
https://www.unified-automation.com/downloads/opc-ua-clients.html.
Click on Server in the Menu
Add
Advanced mode and fill the Configuration Name and the Endpoint URL (replace 192.168.1.100
After confirmation (OK), right-click on the new server name in the Project panel and choose Connect.
Congratulations, you are now connected to your UniPi Axon/Patron! You can now set the DO1 to value true for example. Navigate to Address Space panel and select DO1. In Attributes panel search Value Value, double-click on it, check the radio box and hit Enter. The first Digital outputs LED diod on UniPi Axon/Patron should glow. Detailed tutorial on using OPC UA with REXYGEN is there [3].
After installation of REXYGEN development tools (described in Chapter 2), you can open the REXYGEN Studio on your PC and download algorithm of this default project from your UniPi Axon/Patron.
Select Load Project from Target Device from starting dialog or from File Open Project from Target Device and connect to your UniPi Axon/Patron (replace 192.168.1.100 with the IP address of your UniPi Axon/Patron).
Choose the directory where will be the project stored on your PC and hit OK.
If everything went well, the project algorithm will appear.
The process of creating a control algorithm will be demonstrated on a very simple example with four Boolean variables representing manual switches. In Chapter 7.3, two of them will be replaced by physical inputs of the UniPi Axon/Patron. A software timer will be used for measuring the time when the variables are true (i.e. the switches are in the ON position). A Boolean signal will indicate that the interval of predefined length has elapsed.
- Open Block Library, choose View/Block Library in the menu or use the icon from the toolbar.
The developed algorithm must be compiled to binary form prior to deploying. Pick Project/Compile from the menu or use the icon from the toolbar. The compiler output is displayed in the Compiler window. If no error is found, the myproject_exec.rex file is created.
At this moment it is possible to deploy the control algorithm to the target platform. Use Project/Compile and Download in the menu or click the Compile and Download icon for this purpose. A dialog for defining the target device appears upon successful compilation.
Enter the IP address of your UniPi Axon/Patron in the Target field.
If there is no licence on your UniPi Axon/Patron, you need to get one first. You can get a DEMO licence for free. See Appendix B for details and come back afterwards.
It is also possible to open a Diagnostics view of the algorithm. Pick Target/Diagnostics from the menu or click the icon and you will see the algorithm in a tree view which allows you to monitor the control algorithm in full detail. You can verify that the sampling rate of your algorithm is indeed 100 milliseconds. You can also adjust parameters of individual function blocks, which has the same effect as modifying them directly in the Block properties dialog.
Note: There is also a standalone diagnostics program called REXYGEN Diagnostics. Click the REXYGEN Diagnostics icon and confirm the IP address of the target platform.
Now you can switch REXYGEN Studio back to the Development mode. You can do so by deactivating the Watch mode (use the icon). You are offered synchronization of the changed parameters with the source files of the project, choose No at this moment.
All changes made while in the Watch mode are not permanently stored in the target device (unless you decide so, see [4]). Upon restarting the RexCore runtime module the algorithm will start with the parameters defined in the project source files, which were valid when compiling and downloading the algorithm to the target device. To apply the changes permanently, you have to transfer the changes to the source files and Compile and download the project one more time which defines new startup values.
moment. See [5] for details, it is a very interesting tool for developers and
- See [5] for detailed information about WebBuDi elements and possible customization (colors, backgrounds etc.).
- The default URL address is http://192.168.1.100:8008/hmi/index.html (replace 192.168.1.100 with the IP address of your UniPi Axon/Patron).
We will use the input and output signals of the UniPi Axon/Patron for interaction with the real world.
As mentioned in Chapter 6, two physical switches will be connected as inputs and a software timer will control one output signal. In other words, this chapter is devoted to advancing from the generic example 0101-01 to example 0127-01 for the UniPi Axon/Patron.
Connect the switches as shown below.
Now we tell the compiler to use the UniPi Axon/Patron I/O driver. To do this, edit the IODRV block parameters. Communication will be mediated using Modbus TCP. Link the IODRV block with the MBDrv (Modbus) module by setting
- (beware, it’s CASE SENSITIVE!)
Continue editing the IODRV block parameters. For UniPi Axon/Patron set the following:
As the final step, rename the IODRV block to AXN, which will serve as a prefix for all I/O signals of this driver.
You have to create the axon_cfg.rio file. Click on Configure button and fill the form as shown bellow. After that, click on OK and the file will be stored in the project folder.
In the task double-click the input flag and set . Note the AXN prefix and two underscore characters. The first physical switch (SW1) is connected to first group of Digital Inputs - input 1.
The other physical switch (SW3) is connected to Digital Input 1.3 (AXN__DI1_3). The last (Digital Output) flag will be set as
After compiling the project and downloading it to the UniPi Axon/Patron the control algorithm interacts with the physical world. Again it is possible to switch to Watch mode and observe the signals in real-time or analyze the trends of signals. Flip the physical switches and watch the signals.
A detailed description of the Modbus TCP IO driver which serves as communication platform for UniPi Axon/Patron is available in a separate manual [6].
7.5.2 Examples
Start
from an Example Project and select one of the UniPi Axon/Patron examples. As
Congratulations, you have created the example from scratch! You have learned how to develop, compile and run your algorithms on the UniPi Axon/Patron. The interaction with sensors and actuators is provided via input-output driver of the REXYGEN system, which you have learned to configure and use.
Chapter 6 describes the creation of a simple WebBuDi user interface. The REXYGEN development tools also contain the REXYGEN HMI Designer program which is a tool for designing custom graphical visualizations from predefined components (Definition of custom components is also possible but it requires a bit of Javascript coding.). The REXYGEN HMI Designer is based on the well-known open-source vector editor InkscapeTM https://inkscape.org/en/.
You can find the description of each component and property in [5]. Leave the default values
The Browser requires a target device with running algorithm. Make sure the algorithm is running, see Section 6.2. Also the target URL must be set. Press Browse button. The login dialog will be opened. Change Target to 192.168.1.100:8008 (replace 192.168.1.100 with the IP address of your UniPi Axon/Patron). Unless you changed the login credentials, use the default username admin with an empty password. After a successful login the connection tab is expanded with a tree-view of the running algorithm (you have already seen this tree-view in algorithm diagnostics).
As mentioned earlier, the *.hmi.svg files in the hmisrc folder are automatically processed while the project is compiled in the REXYGEN Studio application. The project main file must contain the HMI block with GenerateRexHMI parameter enabled. This was already covered in Section 6.3 so you should have everything ready.
Once you compile the project again and download it to your UniPi Axon/Patron, the HMI
will be accessible via a web browser. Navigate to
of your UniPi Axon/Patron). You will see your HMI with live data.
This tutorial covers only the very basic components. If you want to get more information about additional components, see [5].
Once successfully applied, your algorithm will download to your UniPi Axon/Patron.
[3] REX Controls s.r.o.. OpcUaDrv driver of REXYGEN – user guide, 2020. .
[4] REX Controls s.r.o.. REXYGEN Studio – User manual, 2020. .
[5] REX Controls s.r.o.. REXYGEN HMI – User manual, 2020. .
[6] REX Controls s.r.o.. Modbus driver of REXYGEN – User guide, 2020. .
Documentation reference number: 14711
2022 © REX Controls s.r.o., www.rexygen.com